Mitsubishi Electric F700 Instruction Manual Page 122

  • Download
  • Add to my manuals
  • Print
  • Page
    / 143
  • Table of contents
  • TROUBLESHOOTING
  • BOOKMARKS
  • Rated. / 5. Based on customer reviews
Page view 121
117
Extended parameters
Extended parameter list
Detection of output frequency
(SU, FU, FU2 signal)
41
Up-to-frequency
sensitivity
0.1% 10% 0 to 100% Set the level where the SU signal turns on.

42
Output frequency
detection
0.01Hz 6Hz 0 to 400Hz
Set the frequency where the FU signal
turns on.

43
Output frequency
detection for
reverse rotation
0.01Hz 9999
0 to 400Hz
Set the frequency where the FU signal
turns on in reverse rotation.

9999 Same as Pr.42 setting
50
Second output
frequency detection
0.01Hz 30Hz 0 to 400Hz
Set the frequency where the FU2 signal turns
on.

44, 45
Refer to Pr. 7 and Pr. 8.
46
Refer to Pr. 0.
47
Refer to Pr. 3.
48, 49
Refer to Pr. 22 and Pr. 23.
50
Refer to Pr. 41 to Pr. 43.
51
Refer to Pr. 9.
Change of DU/PU monitor descriptions
Cumulative monitor clear
52
DU/PU main display
data selection
10
0, 5, 6, 8 to
14, 17, 20, 23
to 25, 50 to
57, 100
Select the monitor to be displayed on the
operation panel and parameter unit.
The setting value of "9" is available only
for the 75K or more.

170
Watt-hour meter
clear
1 9999
0
Set "0" to clear the watt-hour meter monitor.
××
10
Set the maximum value when monitoring
from communication to 0 to 9999kWh.
9999
Set the maximum value when monitoring
from communication to 0 to 65535kWh.
171
Operation hour
meter clear
1 9999 0, 9999
Set "0" in the parameter to clear the watt-
hour monitor.
Setting "9999" has no effect.
×××
268
Monitor decimal
digits selection
1 9999
0 Displays the monitor as integral value.

1 Displays the monitor in increments of 0.1.
9999 No fixed decimal position
563
Energization time
carrying-over times
1 0 0 to 65535
The numbers of cumulative energization
time monitor exceeded 65535h is displayed.
Reading only
×××
564
Operating time
carrying-over times
1 0 0 to 65535
The numbers of operation time monitor
exceeded 65535h is displayed.
Reading only
×××
891
Cumulative power
monitor digit shifted
times
1 9999
0 to 4
Set the number of times to shift the
cumulative power monitor digit
Clamp the monitor value at maximum.

9999
No shift
Clear the monitor value when it exceeds
the maximum value.
Change of the monitor
output from terminal
FM and AM
54
FM terminal
function selection
11
1 to 3, 5, 6, 8
to 14, 17, 21,
24, 50, 52, 53
Select the monitor output to terminal FM.
The setting value of "9" is available only
for the
75k or more.

55
Frequency
monitoring
reference
0.01Hz 60Hz 0 to 400Hz
Set the full-scale value to output the
output frequency monitor value to terminal
FM and AM.

56
Current monitoring
reference
0.01/
0.1A
*9
Rated
inverter
output
current
0 to 500/
0 to 3600A
*9
Set the full-scale value to output the output
current monitor value to terminal FM and AM.
*9 The setting depends on the inverter
capacity (55K or less/75k or more)

158
AM terminal
function selection
11
1 to 3, 5, 6,
8 to 14,
17, 21, 24,
50, 52, 53
Select the monitor output to terminal AM.
The setting value of "9" is available only
for the 75K or more.

867
AM output filter
0.01s 0.01s 0 to 5s Set the output filter of terminal AM.

Func
t
ion
Parameter
Name
Incre
ments
Initial
Value
Range Description
Param
eter
copy
Param
eter
clear
All
param
eter
clear
Related
parameters
: enabled
× : disabled