Extended parameters
Extended parameter list
Slip compensation
245
Rated slip
0.01% 9999
0 to 50% Used to set the rated motor slip.

9999 No slip compensation
246
Slip compensation
time constant
0.01s 0.5s 0.01 to 10s
Used to set the response time of slip
compensation. When the value is made
smaller, response will be faster. However,
as load inertia is greater, a regenerative
overvoltage (E.OV) error is more liable
to occur.

247
Constant-output
region slip
compensation
selection
1 9999
0
Slip compensation is not made in the
constant output range (frequency range
above the frequency set in Pr.3)

9999
Slip compensation is made in the constant
output range.
Selection of motor
stopping method
250
Stop selection
0.1s 9999
0 to 100s
The motor is coasted
to a stop when the
preset time elapses
after the start signal
is turned off.
When 1000s to
1100s is set (Pr. 250
setting-1000)s later,
the motor coasts to
stop.
STF signal:
Forward rotation
start
STR signal:
Reverse rotation
start

1000 to
1100s
STF signal: Start
signal
STR signal:
Forward/reverse
signal
9999
When the start signal
is turned off, the
motor decelerates to
stop.
STF signal:
Forward rotation
start
STR signal:
Reverse rotation
start
8888
STF signal: Start
signal
STR signal:
Forward/reverse
signal
Input/output phase
failure protection
selection
251
Output phase
failure protection
selection
11
0 Without output phase failure protection

1 With output phase failure protection
872
Input phase failure
protection selection
10
0 Without input phase failure protection

1 With input phase failure protection
252, 253
Refer to Pr.73.
Display of the life of the inverter parts
255
Life alarm status
display
1 0 (0 to 15)
Display whether the control circuit
capacitor, main circuit capacitor, cooling
fan, and each parts of the inrush current
limit circuit has reached the life alarm
output level or not.
×××
256
Inrush current limit
circuit life display
1% 100% (0 to 100%)
Display the deterioration degree of the
inrush current limit circuit. Reading only
×××
257
Control circuit
capacitor life
display
1% 100% (0 to 100%)
Display the deterioration degree of the
control circuit capacitor. Reading only
×××
258
Main circuit
capacitor life
display
1% 100% (0 to 100%)
Display the deterioration degree of the
main circuit capacitor. Reading only
The value measured by Pr. 259 is
displayed.
×××
259
Main circuit
capacitor life
measuring
100, 1
Start measuring the main circuit capacitor life.
Switch the power supply on again and
check the Pr. 259 setting. Measurement is
complete if the setting is "3". Set the
deterioration degree in Pr.258.

Func
t
ion
Parameter
Name
Incre
ments
Initial
Value
Range Description
Param
eter
copy
Param
eter
clear
All
param
eter
clear
Related
parameters
: enabled