Causes and corrective actions
5
TROUBLESHOOTING
Operation Panel
Indication
E.OP1 FR-PU04 Option slot alarm 1
Name
Communication option alarm
Description
Stops the inverter output if a communication line error of the communication option occurs.
Check point
· Check for a wrong option function setting and operation.
· Check that the plug-in option is plugged into the connector securely.
· Check for a brake in the communication cable.
· Check that the terminating resistor is fitted properly.
Corrective action
· Check the option function setting, etc.
· Connect the plug-in option securely.
· Check the communication cable connecting.
Operation Panel
Indication
E. 1 FR-PU04
Fault 1
Name
Option alarm
Description
Stops the inverter output if a contact fault or the like of the connector between the inverter and
communication option occurs.
Check point
1. Check that the plug-in option is plugged into the connector securely.
2. Check for excess electrical noises around the inverter.
Corrective action
1. Connect the plug-in option securely.
2. Take measures against noises if there are devices producing excess electrical noises around the inverter.
If the problem still persists after taking the above measure, please contact your sales
representative or distributor.
Operation Panel
Indication
E.PE FR-PU04 Corrupt Memry
Name
Parameter storage device alarm (control circuit board)
Description A fault occurred in parameters stored (EEPROM failure)
Check point Check for too many number of parameter write times.
Corrective action
Please contact your sales representative.
When performing parameter write frequently for communication purposes, set "1" in Pr. 342 to
enable RAM write. Note that powering off returns the inverter to the status before RAM write.
Operation Panel
Indication
E.PE2 FR-PU04 Fault 14
Name
Parameter storage device alarm (main circuit board)
Description
A fault occurred in parameters stored (EEPROM failure)
Check point
——————
Corrective action
Please contact your sales representative.
Operation Panel
Indication
E.PUE FR-PU04 PU Leave Out
Name
PU disconnected
Description
This function stops the inverter output if communication between the inverter and PU is suspended,
e.g. the operation panel and parameter unit is disconnected, when "2", "3", "16" or "17" was set in
Pr. 75 Reset selection/disconnected PU detection/PU stop selection. This function stops the inverter
output when communication errors occurred consecutively for more than permissible number of
retries when a value other than "9999" is set in Pr. 121 Number of PU communication retries during the
RS-485 communication with the PU connector. This function also stops the inverter output if
communication is broken for the period of time set in Pr. 122 PU communication check time interval.
Check point
· Check that the FR-DU07 or parameter unit (FR-PU04) is fitted tightly.
· Check the Pr. 75 setting.
Corrective action
Fit the FR-DU07 or parameter unit (FR-PU04) securely.
Operation Panel
Indication
E.RET FR-PU04 Retry No Over
Name
Retry count excess
Description
If operation cannot be resumed properly within the number of retries set, this function stops the
inverter output.
Check point
Find the cause of alarm occurrence.
Corrective action
Eliminate the cause of the error preceding this error indication.