Wiring
2
INSTALLATION AND WIRING
2.4.2 Specification of main circuit terminal
2.4.3 Terminal arrangement of the main circuit terminal, power supply and the
motor wiring.
200V class
Terminal
Symbol
Terminal Name Description
R/L1,
S/L2,
T/L3
AC power input
Connect to the commercial power supply.
Keep these terminals open when using the high power factor converter
(FR-HC, MT-HC) or power regeneration common converter (FR-CV).
U, V, W Inverter output Connect a three-phase squirrel-cage motor.
R1/L11,
S1/L21
Power supply for
control circuit
Connected to the AC power supply terminals R/L1 and S/L2. To retain
the alarm display and alarm output or when using the high power factor
converter (FR-HC, MT-HC) or power regeneration common converter
(FR-CV), remove the jumpers from terminals R/L1-R1/L11 and S/L2-
S1/L21 and apply external power to these terminals.
Do not turn off the power supply for control circuit (R1/L11, S1/L21) with
the main circuit power (R/L1, S/L2, T/L3) on. Doing so may damage the
inverter. The circuit should be configured so that the main circuit power
(R/L1, S/L2, T/L3) is also turned off when the power supply for control
circuit (R1/L11, S1/L21) is off.
18.5K or less : 60VA, 22K or more : 80VA
P/+, N/-
Brake unit
connection
Connect the brake unit (FR-BU, BU and MT-BU5), power
regeneration common converter (FR-CV), high power factor
converter (FR-HC and MT-HC) or power regeneration converter (MT-
RC).
P/+, P1
DC reactor
connection
For the 55K or less, remove the jumper across terminals P/+ - P1
and connect the DC reactor. (For the 75K or more, a DC reactor is
supplied as standard.)
PR, PX Please do not remove or use terminals PR and PX or the jumper connected.
Earth (ground)
For earthing (grounding) the inverter chassis. Must be earthed
(grounded).
FR-F720-0.75K, 1.5K FR-F720-2.2K to 5.5K
R/L1
S/L2
T/L3
N/-
P/+
PR
PX
R1/L11
S1/L21
As this is an inside cover fixing screw,
do not remove it.
IM
Screw size (M4)
Screw size
(M4)
Jumper
Jumper
Charge lamp
Motor
Power supply
R/L1 S/L2 T/L3
N/-
P/+
PR
PX
R1/L11 S1/L21
IM
Screw size (M4)
Screw size
(M4)
Jumper
Jumper
Charge lamp
Motor
Power supply