Precautions for use of the inverter
2
INSTALLATION AND WIRING
2.6 Precautions for use of the inverter
The FR-F700 series is a highly reliable product, but incorrect peripheral circuit making or operation/handling method
may shorten the product life or damage the product.
Before starting operation, always recheck the following items.
(1) Use crimping terminals with insulation sleeve to wire the power supply and motor.
(2) Application of power to the output terminals (U, V, W) of the inverter will damage the inverter. Never perform such
wiring.
(3) After wiring, wire offcuts must not be left in the inverter.
Wire offcuts can cause an alarm, failure or malfunction. Always keep the inverter clean. When drilling mounting holes
in an enclosure etc., take care not to allow chips and other foreign matter to enter the inverter.
(4) Use cables of the size to make a voltage drop 2% maximum.
If the wiring distance is long between the inverter and motor, a main circuit cable voltage drop will cause the motor
torque to decrease especially at the output of a low frequency.
Refer to page 14 for the recommended cable sizes.
(5) The overall wiring length should be 500m maximum.
Especially for long distance wiring, the fast-response current limit function may be reduced or the equipment connected
to the inverter output side may malfunction or become faulty under the influence of a charging current due to the stray
capacity of the wiring. Therefore, note the overall wiring length. (Refer to page 16.)
(6) Electromagnetic wave interference
The input/output (main circuit) of the inverter includes high frequency components, which may interfere with the
communication devices (such as AM radios) used near the inverter. In this case, set the EMC filter valid to minimize
interference.
(7) Do not install a power factor correction capacitor, varistor or arrester on the inverter output side.
This will cause the inverter to trip or the capacitor, varistor, or arrester to be damaged. If any of the above devices is
installed, immediately remove it.
(8) Before starting wiring or other work after the inverter is operated, wait for at least 10 minutes after the power supply has
been switched off, and check that there are no residual voltage using a tester or the like. The capacitor is charged with
high voltage for some time after power off and it is dangerous.
(9) A short circuit or earth (ground) fault on the inverter output side may damage the inverter modules.
· Fully check the insulation resistance of the circuit prior to inverter operation since repeated short circuits caused by
peripheral circuit inadequacy or an earth (ground) fault caused by wiring inadequacy or reduced motor insulation
resistance may damage the inverter modules.
· Fully check the to-earth (ground) insulation and inter-phase insulation of the inverter output side before power-on.
Especially for an old motor or use in hostile atmosphere, securely check the motor insulation resistance etc.
(10) Do not use the inverter input side magnetic contactor to start/stop the inverter.
Always use the start signal (ON/OFF of STF and STR signals) to start/stop the inverter.
(11) Do not apply a voltage higher than the permissible voltage to the inverter I/O signal circuits.
Contact to the inverter I/O signal circuits or opposite polarity may damage the I/O devices. Especially check the
wiring to prevent the speed setting potentiometer from being connected incorrectly to short terminals 10E-5.
(12) Provide electrical and mechanical interlocks for MC1 and MC2 which are used for commercial power supply-inverter
switch-over.
When the wiring is incorrect or if there is a commercial power supply-inverter switch-over circuit as shown below, the
inverter will be damaged by leakage current from the power supply due to arcs generated at the time of switch-over
or chattering caused by a sequence error.
(13) If the machine must not be restarted when power is restored after a power failure, provide a magnetic contactor in the
inverter's input side and also make up a sequence which will not switch on the start signal.
If the start signal (start switch) remains on after a power failure, the inverter will automatically restart as soon as the
power is restored.
(14) Instructions for overload operation
When performing operation of frequent start/stop of the inverter, increase/decrease in the temperature of the
transistor element of the inverter may repeat due to a continuous flow of large current, shortening the life from
thermal fatigue. Since thermal fatigue is related to the amount of current, the life can be increased by reducing bound
current, starting current, etc. Decreasing current may increase the life. However, decreasing current will result in
insufficient torque and the inverter may not start. Therefore, increase the inverter capacity to have enough allowance
for current.
(15) Make sure that the specifications and rating match the system requirements.
(Refer to page 24)
(Refer to page 8)
Power
supply
Inverter
Undesirable current
MC2
MC1
Interlock
U
V
W
R/L1
S/L2
T/L3
IM