52
Increase the starting torque (Pr. 0)
4.2 Increase the starting torque (Pr. 0)
Set this parameter when "the motor with a load will not rotate", "an alarm [OL] is output, resulting in an
inverter trip due to [OC1], etc.
Parameter
Number
Name Initial Value
Setting
Range
Description
0 Torque boost
0.75K
6%
0 to 30%
Motor torque in the low-
frequency range can be
adjusted to the load to
increase the starting motor
torque.
1.5K to 3.7K
4%
5.5K, 7.5K
3%
11K to 37K
2%
45K, 55K
1.5%
75K or more
1%
Changing example
When the motor with a load will not rotate,
increase the Pr. 0 value 1% by 1% unit by
looking at the motor movement. (The guideline
is for about 10% change at the greatest.)
REMARKS
· A too large setting will cause the motor to overheat, resulting in an overcurrent trip (OL (overcurrent alarm) then E.OC1
(overcurrent shutoff during acceleration)), thermal trip (E.THM (Motor overload shutoff), and E.THT (Inverter overload shutoff)).
When an error (E.OC1) occurs, release the start command, and decrease the Pr. 0 value 1% by 1% to reset. (Refer to page 67.)
POINT
If the inverter still does not operate properly after the above measures, adjust Pr. 80 "Simple magnetic vector
control" [extended mode]. (Refer to the Instruction Manual (applied).)
Output
voltage
P
r. 0
P
r.46
Setting
range
Base
frequency
0
100%
Output
frequency
(Hz)
1.Screen at powering on
The monitor display appears.
Display
Operation
The initial value
differs according
to the capacity.
3.Press to choose the parameter
setting mode.
4.
Pr. 0) appears.
Flicker ··· Parameter setting complete!!
7.Press to set.
PU indication is lit.
2.Press to choose the PU operation mode.
· Press to show the setting again.
· Press twice to show the next parameter.
· By turning , you can read another parameter.
The parameter
number read
previously appears.
6.Turn to change it to the set value
of " ".
5.Press to read the currently set value.
" "(initial value is 6% for the 0.75K)
appears.