Causes and corrective actions
5
TROUBLESHOOTING
(2) Warnings
When the protective function is activated, the output is not shut off.
Operation Panel
Indication
OL FR-PU04 OL
Name
Stall prevention (overcurrent)
Description
During
acceleration
If a current of more than 120% of the rated inverter current flows in the motor, this
function stops the increase in frequency until the overload current reduces to
prevent the inverter from resulting in overcurrent shut-off.
When the overload current has reduced below 120%, this function increases the
frequency again.
During
constant-
speed
operation
If a current of more than 120% of the rated inverter current flows in the motor, this
function lowers the frequency until the overload current reduces to prevent
overcurrent shut-off. When the overload current has reduced below 120%, this
function increases the frequency up to the set value.
During
deceleration
If a current of more than 120% of the rated inverter current flows in the motor, this
function stops the decrease in frequency until the overload current reduces to
prevent the inverter from resulting in overcurrent shut-off.
When the overload current has reduced below 120%, this function decreases the
frequency again.
Check point
1. Check that the Pr. 0 Torque boost setting is not too large.
2. Check that the Pr. 7 Acceleration time and Pr. 8 Deceleration time settings are not too small.
3. Check that the load is not too heavy.
4. Are there any failure in peripheral devices?
5. Check that the Pr. 13 Starting frequency is not too large.
·
Check the motor for use under overload.
Corrective action
1. Increase or decrease the Pr. 0 Torque boost value 1% by 1% and check the motor status. (Refer to page 52.)
2. Set a larger value in Pr. 7 Acceleration time and Pr. 8 Deceleration time. (Refer to page 54.)
3. Reduce the load weight.
4. Try simple magnetic flux vector control (Pr. 80).
5. Change the Pr. 14 Load pattern selection setting.
6. Set stall prevention operation current in
Pr. 22 Stall prevention operation level
. (The initial value is 120%.)
The acceleration/deceleration time may change. Increase the stall prevention operation level with
Pr. 22
Stall prevention operation level
, or disable stall prevention with
Pr. 156 Stall prevention operation selection
.
(Use
Pr. 156
to set either operation continued or not at OL operation.)
Operation Panel
Indication
oL FR-PU04 oL
Name
Stall prevention (overvoltage)
Description
During
deceleration
· If the regenerative energy of the motor becomes excessive and exceeds the
regenerative energy consumption capability, this function stops the decrease in
frequency to prevent overvoltage shut-off. As soon as the regenerative energy
has reduced, deceleration resumes.
· If the regenerative energy of the motor becomes excessive when regeneration
avoidance function is selected (Pr. 882 = 1), this function increases the speed to
prevent overvoltage shut-off. (Refer to the Instruction Manual (applied).)
Check point
· Check for sudden speed reduction.
· Regeneration avoidance function (Pr. 882 to Pr. 886) is being used? (Refer to the Instruction Manual
(applied).)
Corrective action
The deceleration time may change.
Increase the deceleration time using Pr. 8 Deceleration time.
Operation Panel
Indication
PS FR-PU04 PS
Name
PU Stop
Description
Stop with of the PU is set in Pr. 75 Reset selection/disconnected PU detection/PU stop selection.
(For Pr. 75, refer to the Instruction Manual (applied).)
Check point
Check for a stop made by pressing of the operation panel.
Corrective action
Turn the start signal off and release with .