Extended parameters
Extended parameter list
Retry function at alarm occurrence
65
Retry selection
1 0 0 to 5 An alarm for retry can be selected. 
67
Number of retries at
alarm occurrence
10
0 No retry function

1 to 10
Set the number of retries at alarm
occurrence. An alarm output is not
provided during retry operation.
101 to 110
Set the number of retries at alarm
occurrence. (The setting value minus 100
is the number of retries.) An alarm output is
provided during retry operation.
68
Retry waiting time
0.1s 1s 0 to 10s
Set the waiting time from when an inverter
alarm occurs until a retry is made.

69
Retry count display
erase
100
Clear the number of restarts succeeded
by retry.

66
Refer to Pr.22 and Pr.23.
67 to 69
Refer to Pr.65.
70
Refer to Pr.30.
Use the constant
torque motor
(applied motor)
71
Applied motor
10
0
Thermal characteristics of a standard
motor

1
Thermal characteristics of the Mitsubishi
constant-torque motor
2
Thermal characteristic of standard motor
Adjustable 5 points V/F
20
Mitsubishi standard motor (SF-JR 4P
1.5kW or less)
Carrier frequency
and SoftPWM
selection
72
PWM frequency
selection
12
0 to 15/
0 to 6, 25
*12
PWM carrier frequency can be changed.
The setting displayed is in [kHz].
Note that 0 indicates 0.7kHz, 15 indicates
14.5kHz and 25 indicates 2.5kHz.
*12 The setting depends on the inverter
capacity (55K or less/75k or more)

240
Soft-PWM
operation selection
11
0 Soft-PWM invalid

1
When Pr. 72="0 to 5" ("0 to 4" for the 75K or
more), Soft-PWM is valid.
260
PWM frequency
automatic switchover
11
0
PWM carrier frequency is constant
independently of load.
When the carrier frequency is set to 3kHz
or more (Pr. 723), perform continuous
operation at less than 85% of the rated
inverter current.

1
Decreases PWM carrier frequency
automatically when load increases.
Analog input selection
73
Analog input
selection
11
0 to 7,
10 to 17
Input specification (0 to 5V, 0 to 10V) of
terminal 2 and 1 can be selected.
Override and reversible operation can be
selected.
×
242
Terminal 1 added
compensation
amount (terminal 2)
0.1% 100% 0 to 100%
Set the ratio of added compensation
amount when terminal 2 is the main
speed.

243
Terminal 1 added
compensation
amount (terminal 4)
0.1% 75% 0 to 100%
Set the ratio of added compensation
amount when terminal 4 is the main
speed.

252
Override bias
0.1% 50% 0 to 200%
Set the bias side compensation value of
override function.

253
Override gain
0.1% 150% 0 to 200%
Set the gain side compensation value of
override function.

267
Terminal 4 input
selection
10
0 Terminal 4 input 4 to 20mA
×
1 Terminal 4 input 0 to 5V
2 Terminal 4 input 0 to 10V
Func
t
ion
Parameter
Name
Incre
ments
Initial
Value
Range Description
Param
eter
copy
Param
eter
clear
All
param
eter
clear
Related
parameters
: enabled
× : disabled